3. Example
A Wall pipe, with louvred vent
= 1 x 3.8 m Additional duct
length
= 3.8 m
B/D 2 Elbows, 90°
= 2 x 0.8 m Additional duct
length
= 1.6 m
C 0.5 m plastic piping
= 0.5 x 1 m Additional duct
length
= 0.5 m
E Side connection, left
= 1 m Additional duct length = 1.0 m
Effective duct length = 6.9 m
Result: A duct diameter of 100 mm is
adequate as the effective duct length is
less than the 20 m specified in Table II.
Installation to the left or right
side of the machine
At the rear
The connection is opened at the
factory.
^
Fit one of the venting systems
described on the following pages.
Left or right side of the machine
^
Remove the left or right hand side
cover cap. Do not remove the frame.
Refit it in the rear outlet.
^
Ensure it is securely in position so
that it cannot fall out when the dryer
is in operation.
^
Fit one of the venting systems
described on the following pages.
Installation - venting
38